疏散通道上常闭式防火门是否需要防火门监控?

按火报规范疏散通道上常闭式防火门是需要防火门监控的,但是建规中6.5.1中对常闭式防火门没有明确设计监控要求,

在工程实际中,如何落实,

不需要监控吗?

消防网友78337 | 2021-06-08 12:14
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

窝窝头 2021-06-10 08:40 00 [回复]举报

火灾自动报警系统设计规范GB50116-2013第4.6.1.2疏散通道上各防火门的开启、关闭及故障状态信号应反馈至防火门监控器。

火报规范比建火规对防火门监控更细化,所以应该从严按火报规,建火规本来就只是写了大方向。

AARON 2021-09-13 17:31 00 [回复]举报

好多公共场所的防烟楼梯间是不是应该改为常开防火门?

tjxf888888 2021-11-11 13:45 00 [回复]举报

可以搜一下石老师的消防专题,不是所有防火门都需要监控的,公安部有个答复意见