商业与办公疏散问题

建筑一至二层为商业性质,三至三十二层为办公性质,属于一类高层建筑,商业与办公的疏散楼梯分开独立设置,办公两个独立防烟楼梯间,商业两个独立封闭楼梯间。楼上办公的疏散楼梯间设有防烟前室,楼下商业疏散楼梯间因与敞开外廊相连未设置防烟前室,为封闭楼梯间。我的项目位于二层商业(塔楼正下方),为成人培训学校。请问疏散距离要按高层的计算吗?是否可以按照多层疏散距离计算?

成啊 | 2024-09-06 18:06
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

我头发贼黑 2024-09-07 08:38 00 [回复]举报

高层

成啊   回复: 我头发贼黑2024-09-11 10:22

为何

0    0 [回复]举报

我头发贼黑   回复: 成啊2024-09-11 16:22

改一下,按照多层,楼下是对的

0    0 [回复]举报

磊中 2024-09-07 10:14 20 [回复]举报

我觉得应该是按照多层的来设计吧,

一、本场所与以上楼层做了完全的防火分隔,

二、本场所的疏散设施与以上楼层都独立设置

顾本场所的疏散设施可按多层公共建筑来设计

阳明心   回复: 磊中2024-09-09 08:16

有道理的

0    0 [回复]举报

phone0224 2024-09-13 14:34 00 [回复]举报

浙江省消防有专门的规定,供参考