如何理解“甲类物品仓库宜单独设置;当其储量小于5t时,可与乙、丙类物品仓库共用一座建筑物,但应设独立的防火分区”

GB50160第6.6.1条第1项规定“甲类物品仓库宜单独设置;当其储量小于5t时,可与乙、丙类物品仓库共用一座建筑物,但应设独立的防火分区”。

“甲类物品仓库宜单独设置”很好理解,但是后半句“当其储量小于5t时,可与乙、丙类物品仓库共用一座建筑物,但应设独立的防火分区”的解释,是“当甲类物品少于5t,不独立设置甲类库,可在乙丙类仓库内储存,但是乙丙类仓库要单独设置储存甲类物品的防火分区、甲类物品储量要少于5t”,还是“甲类仓库同时储存甲乙丙类物品时,甲类物品与乙丙类物品要分别储存在不同的防火分区”。

18242099864 | 2024-07-31 14:25
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 6

香.香 2024-07-31 17:14 00 [回复]举报

后半句是指有些场所在某些环节会用到甲类的物品,他们又需要有一定的存量。比如说修车库、手表厂等,这时候就需要将这些甲类物品与其它物品使用防火墙,划分单独的防火分区来存储

18242099864   回复: 香.香2024-07-31 18:20

感谢解惑

0    0 [回复]举报

18242099864   回复: 香.香2024-08-01 10:59

您好,如果设置了甲类仓库,但是乙丙类的物品较少,需要存到甲类库里面,在物品间没有禁忌的情况下,是否可储存在一个防火分区内。

0    0 [回复]举报

香.香   回复: 182420998642024-08-01 16:41

同一座仓库或仓库内的同一防火分区储存有不同火灾危险性的物品的时候,当以火灾危险性大的物品来确定该仓库或防火分区的火灾危险性。不同火灾危险性的物品放到仓库里或仓库内的同一防火分区内,要做好不同物品之间的分隔措施,比如分隔、分库等。但是一般甲乙都是比较危险的物品,最好不要和丙类物品放在一起。他们之间容易发生化学反应,且灭火方式不同。抛开这些危险性不谈,就单纯回答你想问的意思:是可以放一起的。

0    0 [回复]举报

我是小鱼鱼 2024-08-07 16:13 00 [回复]举报

如果甲类物品小于5T,和乙丙类物品共用一座建筑物,那这个“建筑物”定性是“甲类仓库”还是“乙类仓库”?


18242099864   回复: 我是小鱼鱼2024-08-16 10:33

建筑物是储存甲类1.2.5.6项的甲类化学品库

0    0 [回复]举报