消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

简单的60平方生产中控室或者叫调度室集控室必须装自动灭火?

现场就一个网络连接柜,与一排电脑办公桌与挂墙显示屏,已经配置火灾自动报警与室内消火栓,建筑为中央空调单多层办公楼,其他区域都有自动喷水。因为为了装修好看与形象,拆了原本的七氟丙烷自动灭火系统封闭墙做成开放空间。后面为了维保与检查规范,想做消防设计变更

林饕咖 | 2024-06-30 11:24
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 3

潘天坤 2024-07-01 18:05 00 [回复]举报

不确定为什么这个中控室/调度室要设计自动灭火系统,不过如果把七氟丙烷气体灭火系统取消,属于取消整个消防系统,可能需要重新送消防技术审查及消防设计审查

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

3211233 2024-07-02 14:42 00 [回复]举报

石化规条文解释8.11.3条有不设置自动灭火的依据,24小时值班控制室我们一般不设置自动灭火

林饕咖   回复: 32112332024-07-25 15:37

最终核实是因为中央空调系统,与建筑总面积超过3000平,所以导致如果取消气体灭火,要更改为自动喷淋,就是必须设置自动灭火。要不设计院的人不给出变更图

0    0 [回复]举报

关闭

关闭

手机APP下载