消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

建筑是否需要设置自喷的问题

各位专家,一栋独立的单层商业建筑,建筑面积超过了1500平方,分隔成若干个并排的200平方左右小商铺,相互之间采用实体墙完全分隔,每个商铺的出口均独立且面向市政道路。这种建筑需要设自喷吗?如果不需要,有没有相关的依据呢?谢谢指教!

我已不是我 | 2024-04-02 17:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 7

消防网友62921 2024-04-05 01:50 00 [回复]举报

需要。查阅建规8.3。

懒得说 2024-04-05 07:41 00 [回复]举报

规范没有明确要求设置喷淋,不需设置

shawu 2024-04-05 14:38 00 [回复]举报

如果分隔措施满足建规防火间距不限的情况可以不设自喷,此时可按照多座建筑贴邻建造,如果不满足防火间距不限情况自喷还是要设置的,此时还是按照一整座建筑对待


途安008 2024-04-05 15:03 00 [回复]举报

需要设

哇哈哈119 2024-04-05 16:10 00 [回复]举报

1、需要自喷:把建筑当做一个整体,单层大于1500的商店,要自喷。

2、不需要自喷:把每个商铺单独来看,面积200方,不需要设自喷,但需要考虑防火间距的问题,涉及距离调整,防火墙+1.0h顶+一二级耐火等级(适用两栋建筑高度相等,距离不限的情况)

北洼 2024-04-07 16:51 00 [回复]举报

参考商业服务网点设计,不需要设置,但后期隔墙不能打通。

南明离火 2024-04-15 17:18 00 [回复]举报

有看过答疑,类商业服务网点的公建,可以参照住宅的商业服务网点要求来设置。不需要设置


关闭

关闭

手机APP下载