消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

地下防护区和无窗或设固定窗扇的地上防护区,应设置机械排风装置,机械排风装置的控制开关设置位置?

地下防护区和无窗或设固定窗扇的地上防护区,应设置机械排风装置,机械排风装置的控制开关设置位置?有没有明确的条文规定?

永锅 | 2023-07-06 11:27
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0

回答 | 3

安洪全 2023-07-06 14:18 00 [回复]举报

建筑防烟排烟系统技术标准 GB51251-2017

6.4.3 常闭送风口、排烟阀或排烟口的手动驱动装置应固定安装在明显可见、距楼地面1.3m~1.5m之间便于操作的位置,预埋套管不得有死弯及瘪陷,手动驱动装置操作应灵活。


消防资源网 2023-07-06 17:02 00 [回复]举报

你这个是《气体灭火系统设计规范》 GB50370-2005的条文:

6.0.4 灭火后的防护区应通风换气,地下防护区和无窗或设固定窗扇的地上防护区,应设置机械排风装置,排风口宜设在防护区的下部并应直通室外。通信机房、电子计算机房等场所的通风换气次数应不少于每小时5次。


开关设置在门口即可

《气体灭火系统设计规范》 GB50370-2005

周家斌 2023-07-07 09:28 00 [回复]举报

你的描述估计是气体灭火的防护区,

关闭

关闭

手机APP下载