建筑物有防烟排烟系统是否就要上火灾报警系统?

建筑防烟排烟系统技术标准 GB51251-2017 >中

5.1.1 机械加压送风系统应与火灾自动报警系统联动,其联动控制应符合现行国家标准《火灾自动报警系统设计规范》GB 50116的有关规定。

5.1.2 加压送风机的启动应符合下列规定:    

1 现场手动启动;    

2 通过火灾自动报警系统自动启动;    

3 消防控制室手动启动;    

4 系统中任一常闭加压送风口开启时,加压风机应能自动启动。

规范要求送风系统需和火灾报警系统联动,但按《火灾自动报警系统设计规范》不需设置火灾报警系统的建筑物,哪怕是2层的建筑物,设置了防烟排烟系统就需上一套火灾报警系统?

如鱼得水 | 2023-06-28 15:32
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

同同不同 2023-06-29 08:31 00 [回复]举报

是的,有消防联动设备就得配自动报警系统

安洪全 2023-06-29 08:49 00 [回复]举报

是的,设排烟系统必设“火报”。

如鱼得水   回复: 安洪全2023-07-06 10:47

8.2.1 下列部位应采取防烟措施:     1 封闭楼梯间;     2 防烟楼梯间及其前室;     3 消防电梯的前室或合用前室;     4 避难层、避难间;     5 避难走道的前室,地铁工程中的避难走道。

扩建工程,2层小房子,一头的楼梯间开不了窗就要设防烟了,就要上火灾报警了。

0    0 [回复]举报

壹壹 2023-06-29 11:04 00 [回复]举报

个人理解,建筑物设置机械排烟,则必须配备相应的火灾自动报警系统实现联动,这与建筑物的层数无必然联系,既然通风空调专业设置了机械排烟,说明建筑物的火灾风险是比较高的

如鱼得水   回复: 壹壹2023-07-06 08:34

机械排烟并不代表火灾风险高,只是楼梯间密闭,开不了窗。火灾发生是排烟用的。

0    0 [回复]举报

潘天坤 2024-06-26 18:17 00 [回复]举报

是否需要设置火灾自动报警系统,设置条件是看建规及建筑防火通用规范

如果有机械排烟和机械加压送风系统等需与火灾自动报警系统联锁动作的场所或部位,应设置火灾自动报警系统

建筑设计防火规范 GB50016-2014(2018年版)第8.4.1条规定:

下列建筑或场所应设置火灾自动报警系统: 13 设置机械排烟、防烟系统,雨淋或预作用自动喷水灭火系统,固定消防水炮灭火系统、气体灭火系统等需与火灾自动报警系统联锁动作的场所或部位

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

LHH2737 2024-06-27 16:34 00 [回复]举报

有机械防排烟系统时必须设置自动报警系统,而且必须采用集中报警系统