消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

《建筑防火通用规范》防火分区建筑面积歧义,求解答

《建筑防火通用规范》4.3.16 - 4 当防火分区全部设置自动灭火系统时,上述面积可以增加1.0倍;当局部设置自动灭火系统时,可按该局部区域建筑面积的1/2计入所在防火分区的总建筑面积。


局部设置自动灭火系统时,是增加一半的面积,还是只计入一半(还是原来增加1倍的意思)?

这话很有歧义啊,要增加一半就直接写加一半就好了,还故意写的模棱两可的!

消防网友67116 | 2023-04-03 23:11
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

陈曲 2023-04-07 12:39 00 [回复]举报

你说的有道理 以后不要说了 

是各算各的意思 局部按局部折半

消防网友28583 2023-05-11 17:46 00 [回复]举报

这个应该和GB50016建规不矛盾,“当局部设置自动灭火系统时,可按该局部区域建筑面积的1/2计入所在防火分区的总建筑面积。”这句话的意思应该是复核防火分区面积有没超标时,遇到局部设自动灭火系统时,局部那块儿面积减半后再和没设系统的那部分面积相加,两者之和不大于规范规定即可。例如,,多层商场防火分区面积要求不超过2500,某分区建筑面积共2800,其中有800设自喷2000没设自喷,复核防火分区面积是否合格?计算步骤:800/2+2000=2400,不大于2500所以合格。

关闭

关闭

手机APP下载