消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

员工宿舍楼喷淋设置

请问多层员工宿舍楼建筑,不设置集中空调通风系统的,需要设置喷淋和火灾报警系统吗?谢谢!

祥子 | 2022-09-12 15:03
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

永锅 2022-09-13 09:19 20 [回复]举报

员工宿舍的火灾危险性与旅馆建筑的火灾危险性相似,可参照建筑设计防火规范8.3.4.2条、8.4.7条的规定确认是否设置喷淋和火灾报警系统。

个人观点,仅供参考!

消防黄河 2022-09-13 09:23 20 [回复]举报

不。

飞翔的二师兄 2022-09-13 17:22 20 [回复]举报

参考建筑设计防火规范 GB50016-2014(2018年版)8.4条,没有其他需要联动的消防设施,可以不设置自动报警系统;

参考8.3.3和8.3.4条,8.3.3 除本规范另有规定和不宜用水保护或灭火的场所外,下列高层民用建筑或场所应设置自动灭火系统,并宜采用自动喷水灭火系统:     1 一类高层公共建筑(除游泳池、溜冰场外)及其地下、半地下室;     2 二类高层公共建筑及其地下、半地下室的公共活动用房、走道、办公室和旅馆的客房、可燃物品库房、自动扶梯底部;     3 高层民用建筑内的歌舞娱乐放映游艺场所;     4 建筑高度大于100m的住宅建筑。 8.3.4 除本规范另有规定和不适用水保护或灭火的场所外,下列单、多层民用建筑或场所应设置自动灭火系统,并宜采用自动喷水灭火系统:      1 特等、甲等剧场,超过 1500 个座位的其他等级的剧场,超过 2000 个座位的会堂或礼堂,超过 3000 个座位的体育馆,超过 5000 人的体育场的室内人员休息室与器材间等;      2 任一层建筑面积大于 1500m² 或总建筑面积大于 3000m² 的展览、商店、餐饮和旅馆建筑以及医院中同样建筑规模的病房楼、门诊楼和手术部;      3 设置送回风道(管)的集中空气调节系统且总建筑面积大于 3000m² 的办公建筑等;      4 藏书量超过 50 万册的图书馆;      5 大、中型幼儿园,老年人照料设施;      6 总建筑面积大于 500m² 的地下或半地下商店;      7 设置在地下或半地下或地上四层及以上楼层的歌舞娱乐放映游艺场所(除游泳场所外),设置在首层、二层和三层且任一层建筑面积大于 300m² 的地上歌舞娱乐放映游艺场所(除游泳场所外)。可不设置自动喷水灭火系统

关闭

关闭

手机APP下载