消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防干管上一定要装低压压力开关吗

本建筑是2012年造的一类高层公共建筑(办公大楼),消火栓按钮是6根线(信号线,启泵线,回答线)可以连锁直接启动消防泵,未设置低压压力开关。问下同行,这样的情况你们都需要甲方整改设置低压压力开关吗?

wangge1986n | 2022-05-09 16:01
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

周家斌 2022-05-09 19:38 20 [回复]举报

如果不涉及到扩建、改造。维持原系统按照原规范要求保持系统的正常工作。

wangge1986n   回复: 周家斌2022-05-10 20:43

如果是老规范的,消火栓按钮可以直接连锁直接启泵的,个人觉得低压压力开关可以不设置

但是新规范要设置,可是新规范消火栓按钮只是只是作为报警信号,需要联动来启泵,所以他要设置低压压力开关。

0    0 [回复]举报

周家斌   回复: wangge1986n2022-05-11 12:50

按照你的描述,是系统改造了,执行新标准!

1    0 [回复]举报

关闭

关闭

手机APP下载