消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

防火墙处的梁,需要建筑给结构提条件吗?

防火墙处梁耐火极限3h,保护层厚度达50mm(建规第433页,40厚2.9h),需要结构特别处理,对吧?

haizi787 | 2025-03-24 17:12
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

重庆消防 2025-03-25 09:04 00 [回复]举报

需要。现场就有建筑与结构未沟通出现的问题,比如:梁柱影响疏散宽度。

闲淡潮人 2025-03-25 09:32 00 [回复]举报

防火墙处的梁,需要建筑把防火墙的位置提资给结构!然后结构一般采取2种方案;1、保护层直接做到42厚(3.0h)及以上;2、保护层做20-30厚,剩余厚度会由建筑粉刷层来凑。如果结构采取第二种方案,也需要提醒建筑补充节点或自己补充节点。最后,建筑还可以采用在梁周边包防火板的做法,成本不高。

vicher 2025-03-31 16:52 00 [回复]举报

建议先区分清楚简支梁跟连续梁的概念,《建筑设计防护规范》仅对简支梁提出要求;对于上部设有防火墙的连续砼梁,满足《混凝土结构耐火性设计标准》相关要求即可。

关闭

关闭

手机APP下载