消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

排烟风机出口与防烟楼梯间可开启外窗的最近边缘水平距离

各位专家好,就是我们这边有一栋建筑的设计图,在二层设置了一台排烟风机,但是排烟风机的出口处与防烟楼梯间的可开启外窗最近边缘水平距离才2.6米。一旦发生火灾这个排烟风机排出的烟气正好遇到一股向防烟楼梯间可开启外窗方向的风,那么此时窗户正处于打开的时候烟气就会进入防烟楼梯间了,楼内人员就会少一个安全出口。可设计却认为规范没有明确排烟风机出口与防烟楼梯间可开启外窗的最近边缘水平距离,请问大家怎么办呀?

南方人 | 2025-03-21 16:20
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

潘天坤 2025-03-21 16:35 00 [回复]举报

规范里相关要求是在机械加压送风系统和机械排烟系统章节,提到的也都是机械间的关系

如果楼主认为自然通风也需要满足的话,可以跟项目沟通下是否有条件将风机移位



EHS专家-DL 2025-03-21 16:38 00 [回复]举报

一方面还是尽量跟审计单位沟通设计调整当然最好,至少可以考虑调整排烟风机出口方向‌:将排烟口改为垂直向上或背向楼梯间外窗方向,避免直接水平排放。增加导流措施‌:在排烟风机出口处设置挡烟垂壁或导流板,引导烟气远离外窗。再不济通过强化防烟措施来降低因距离较近烟气进入防烟楼梯间影响:加强楼梯间正压送风‌:通过增大送风量或优化送风口位置,确保外窗附近维持足够正压(一般≥25Pa)。控制外窗启闭逻辑‌:若外窗为自然排烟口,需与排烟风机联动,确保火灾时外窗仅在排烟风机未启动时开启。


一般排烟口与外窗的水平距离非强制性经验值为≥4.5m。若设计方坚持原方案,建议委托第三方进行‌CFD烟气模拟‌或组织专家评审,验证极端情况下(如不利风向)的烟气扩散路径,以数据支撑设计修改需求。或者在施工图审查或消防验收阶段,明确向住建部门或消防技术服务机构提出异议,要求按“性能化设计”原则补充安全论证。

李勤 2025-03-24 11:28 00 [回复]举报

关闭

关闭

手机APP下载