消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

高层公共建筑办公区疏散走道两侧墙为普通玻璃墙是否可行

按技术指南4.1.15疏散走道两侧墙的耐火极限小于1.0h时,从房间任一点至安全出口的疏散距离不应大于30m,是否只要满足这个30m就可以采用普通玻璃

最强生物 | 2025-03-20 16:51
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

重庆消防 2025-03-21 08:48 10 [回复]举报

房间内通道为我们常说的疏散通道是最危险区域,次危险区域为疏散走道,疏散走道具有一定防烟功能,普通玻璃不具备防烟功能,所以不行。

最强生物   回复: 重庆消防2025-03-24 10:10

现在很多设计意思都是不需要防火玻璃,所按这个不大于30m就行了。

0    0 [回复]举报

wetom 2025-03-21 09:09 10 [回复]举报

你说的30米是应该是按大空间疏散原则(有喷淋的话是37.5米),根据规范适用于观众厅、展览厅、多功能厅、餐厅、营业厅。个人理解办公也适用,具体的咨询当地验收人员意见。

最强生物   回复: wetom2025-03-24 10:12

就是你说的这个意思。好像每个地区的解释都不一样,浙江这边好像可以设普通玻璃,按大空间这样。一般都是筒式结构的办公楼,然后为了采光好,漂亮,省成本这样设置的。

0    0 [回复]举报

静安消防 2025-03-21 10:47 10 [回复]举报

有见过一种情况,一层面积比较大的厂房,中间是走道,走道两侧的墙体除了梁柱承重墙是整片的玻璃,两边划分不同的作业区,研发,测试,小件加工,属于电子零配件按丙类,但整体可燃物很少很少(给人一种这么干净稍显空旷的厂房,房租这么贵,咋赚钱啊,操心的有点多哈),实际情况确实不好定义啊

消防网友62117 2025-03-25 09:26 00 [回复]举报

办公区内的内部走道可用普通玻璃隔墙,面临核心筒及核心筒走道的隔墙要满足1.0h耐火极限,这是把整个办公区视为一个大房间,采用办公区任意一点到安全出口距离不大于30+10的疏散计算

闲淡潮人 2025-03-25 10:32 00 [回复]举报

个人理解:

如果玻璃隔断形成完整的疏散走道,且直接通往安全出口的话,应该不能钻这个空子,玻璃就需要同时具备耐火、隔热要求。

如果是大空间+部分玻璃房,局部区域形成疏散走道的话,可以采用普通玻璃。

关闭

关闭

手机APP下载