消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

一类高层上面办公,下面有酒店,桌球,KTV,商业等,是否有规范要求明确要求下面各层疏散楼梯独立设置,电梯门洞封死?酒店电梯是否可以与办公共用?

     
| 2025-03-09 10:56
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

重庆消防 2025-03-10 09:07 10 [回复]举报

没有明文规定,你上述的情况是上面为住宅的情况,要求疏散分别独立设置。

LHH2737 2025-03-10 09:33 10 [回复]举报

办公和商业合建,分别布置在不同楼层时可以共用一部疏散楼梯,布置在同一层时则不行;

办公建筑设计标准 JGJ/T67-2019 

5.0.2 办公综合楼内办公部分的安全出口不应与同一楼层内对外营业的商场、营业厅、娱乐、餐饮等人员密集场所的安全出口共用。

小唐12321 2025-03-10 09:34 00 [回复]举报

下面不是按裙房设计一般不要,主要还是看设计图纸

我来也 2025-03-10 11:34 00 [回复]举报

独立出口只有电影院和儿童活动场所有要求!

关闭

关闭

手机APP下载