消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

现场由水井给消防水池给水,水井内深水泵需不需要联动启泵?

请教各位大佬,现场由水井给消防水池给水,水井内深水泵需不需要联动启泵?

请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

小唐12321 2025-02-25 09:50 10 [回复]举报

不需要,规定时间内能补满,然后低于最低水位要及时补水。

潘天坤 2025-02-25 09:50 00 [回复]举报

根据楼主的描述,应该不属于消防水泵,消水规GB50974里没有这类泵的要求

喧哗 2025-02-25 09:52 00 [回复]举报

规范没有强制要求,个人认为,如果稳压泵是从消防水池吸水,就需要联动给消防水池补水。如果仅消防泵从消防水池吸水,消防水泵不运行,也不自动巡检,那么按规范定期进行消防水位检查,可不进行联动水井深井泵。

赖峰 2025-02-25 10:10 00 [回复]举报

这个需要落实下,消防水池有效容积计算时是否考虑了自动补水量,如果没有考虑,无需联动启泵。如果无法落实,需要自己计算

参考
消防给水及消火栓系统技术规范 GB50974-2014 第3.6.1和第4.3.2

huanglong3721 2025-02-25 15:06 00 [回复]举报

应安装水位控制联动补水泵,不应由火灾自动报警系统来联动。

关闭

关闭

手机APP下载