消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防泵每次启动都需要输入密码,符合要求吗

每次手动启动消防泵,都需要输入密码,请问规范上有明确消防泵启动不能设置密码的吗?如有,请附上规范要求

亲亲子衿 | 2025-01-22 11:30
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 7

安洪全 2025-01-22 13:57 00 [回复]举报

没说不能设,但无论是设密码还是其它防止误启动的措施,都“应确保在火灾时能及时启动”

yhue119 2025-01-22 14:22 00 [回复]举报

不符合要求

阿龙 2025-01-22 14:33 00 [回复]举报

规范还要求消防水泵控制柜必须设置机械应急启泵装置,这个不需要密码,火灾时没有自动启可以用

小唐12321 2025-01-22 14:35 00 [回复]举报

个人觉得不合适,假如紧急情况没密码呢,但是如果有机械应急也说得过去。

徐海金 2025-01-22 16:26 00 [回复]举报

给排水通规都要求给水泵房要上物理防护措施了,泵房的门都要密码或锁。都是专业人员操作的,设置柜子设置密码没有毛病。

喧哗 2025-01-22 17:11 00 [回复]举报

个人意见,无人值守消防泵房门平时都是锁着的,消防泵房每次进去都需要钥匙,所以消防泵启动也需要密码挺正常。

小唐12321   回复: 喧哗2025-01-23 08:19

从实际出发,很多水泵房就电工知道密码,假如那天没上班,多少水泵房是打自动的,打自动也很多不能启泵,所以如果我检查就要求旁边贴上密码。

0    0 [回复]举报

关闭

关闭

手机APP下载