消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消火栓按钮需要启动消防泵

对于丁类厂房可以不设火灾自动报警系统。可以参考问题集锦问题206。不设火灾报警系统的消火栓按钮需要启动消防泵。


在实际问题中,建筑体中无火灾自动报警系统的丁类仓库群,有300余室内消火栓,其消火栓按钮直接连线到消防泵控制柜,(以总线方式),如何连线呢,


用多线方式,300多组线如何连续呢?

消防网友78337 | 2021-04-19 09:06
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

刘丽波 2021-04-20 11:33 10 [回复]举报

我对电气专业不太通。在13版的火灾自动报警实施以前,都是消防按钮启动消防泵,那时候怎么设置就怎么做。可以参考一下上一版图示。

14555 2021-04-20 23:17 00 [回复]举报

临时高压消防给水系统可由高位水箱的流量开关、消防水泵出水干管上的压力开关、报警阀压力开关直接启动消防水泵。规范说的是不宜并没有说禁止,原因是投入资金较大不符合经济适用的原则。

牛疼 2021-04-22 16:56 00 [回复]举报

泵控柜的接触器外设置2套继电器,同时消火栓按钮设置独立的电源,由消火栓按钮控制继电器,继电器控制接触器的辅助触点来保证启泵功能。  

我认为只是常开点常闭点的使用。

防火防盗防闺蜜 2021-05-11 22:58 00 [回复]举报

可以在消火栓出水干管设置湿式报警阀,压力开关连锁启动水泵

关闭

关闭

手机APP下载