消防水池溢流管预埋留套管为什么留在有效水位以下?还要往上做个管子达到溢流水位?

消防网友33186 | 2024-11-07 16:09
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

消防网友33186 2024-11-15 13:33 00 [回复]举报

有谁回答一下啊?

大悟无言 2024-11-21 16:15 00 [回复]举报

该做法是根据《建筑给水排水设计标准 GB50015-2019 》3.8.6中第5款: 溢流管宜采用水平喇叭口集水,喇叭口下的垂直管段长度不宜小于4倍溢流管管径;溢流管的管径应按能排泄水池(箱)的最大入流量确定,并宜比进水管管径大一级;溢流管出口端应设置防护措施;

至于为何会这样规定,个人理解是喇叭口方便集水顺利排出,如果直接在有效水位或者以上开洞,会导致集水不畅,排水过慢,池内水超过设计容积,增加荷载或者淹没进水管产生水污染等隐患。