消防问答 > 其他 提问

消防电路不能设置过载保护,只能设置短路保护是在哪个规范里规定的

消防电路不能设置过载保护,只能设置短路保护是在哪个规范里规定的

请写下您的回答回答

הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


共 3 回答

EHS专家-DL 25-04-02

现行规范中,《民用建筑电气设计标准》GB51348-2019第7.6.3条和《建筑电气与智能化通用规范》GB55024-2022第4.3.7条是明确禁止消防线路设置过载切断保护的核心依据,要求仅保留短路保护功能,过载时仅允许报警‌。

2 0 [回复]举报

潘天坤 25-04-02

火灾自动报警系统的控制主机的主电源可以按照火灾自动报警系统设计规范 GB50116的要求,“火灾自动报警系统主电源不应设置剩余电流动作保护和过负荷保护装置”执行


消防水泵、防排烟风机等的配电线路可以按照民用建筑电气设计标准 GB51348及建筑电气与智能化通用规范GB55024的要求,“消防水泵、防排烟风机等的配电线路不设置过负荷保护,当设置时只能动作于报警”执行




1 0 [回复]举报

李勤 25-04-02

0 0 [回复]举报

最新问题

关闭

关闭