一类高层消防屋面稳压泵启停压力设置多少合符规范要求,这条规范在那里可以查到

一类高层消防屋面稳压泵启停压力设置多少合符规范要求,这条规范在那里可以查到

shunli | 2024-07-02 23:23
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

安洪全 2024-07-03 14:48 00 [回复]举报

消防给水及消火栓系统技术规范 GB50974-2014

5.3.3 稳压泵的设计压力应符合下列要求:     

1 稳压泵的设计压力应满足系统自动启动和管网充满水的要求;    

2 稳压泵的设计压力应保持系统自动启泵压力设置点处的压力在准工作状态时大于系统设置自动启泵压力值,且增加值宜为0.07MPa~0.10MPa;    

3 稳压泵的设计压力应保持系统最不利点处水灭火设施在准工作状态时的静水压力应大于0.15MPa。


香.香 2024-07-04 16:25 01 [回复]举报

稳压泵的启停压力需要计算确定,当稳压泵设置在屋面时和设置在地下时计算方法是不一样的。通过计算得出结果且满足大于1L/S,同时满足系统自动启动和管网充满水的要求。计算出了稳压泵的启停压力也就可以计算出水泵的低压压力开关的启泵值了